• Welcome, Guest! We hope you enjoy the excellent technical knowledge, event information and discussions that the BMW MOA forum provides. Some forum content will be hidden from you if you remain logged out. If you want to view all content, please click the 'Log in' button above and enter your BMW MOA username and password.

    If you are not an MOA member, why not take the time to join the club, so you can enjoy posting on the forum, the BMW Owners News magazine, and all of the discounts and benefits the BMW MOA offers?

  • Beginning April 1st, and running through April 30th, there is a new 2024 BMW MOA Election discussion area within The Club section of the forum. Within this forum area is also a sticky post that provides the ground rules for participating in the Election forum area. Also, the candidates statements are provided. Please read before joining the conversation, because the rules are very specific to maintain civility.

    The Election forum is here: Election Forum

Federal Pacific Electrical panel issues

henzilla

not so retired
Staff member
Have known there were issues with FPE ( Federal Pacific Electric) breaker panels for years.
Last night the news ( have not found that story yet) had another story about the sleeping danger in a lot of homes .
I have had a few calls from older neighbors asking me to see what they have...luckily, the 5 panels on our property are GE.
I changed my moms FPE panel out in the 90's after a few issues showed up.


The typical response '' I have had mine for 50 years and no problems'' has bitten a few folks, or might as it only takes one bad electrical fault. Not trying to scare anybody, but something to think about. Not a cheap fix...but I changed my moms for peace of mind:thumb

In Houston area, the use of Sylvania/Zinsco breakers and aluminum circuit wiring in the 70's had us going to fire calls and trouble calls after a lightning storm with a lot of holes blown in sheetrock and burnt panels. We used to shudder when troubleshooting customer issues when seeing the green and red Zinsco breakers staring at us.Aluminum wiring wasn't terminated at breakers and outlets/fixtures correctly as no one really gave it a lot of thought.Another issue in itself
http://www.ismypanelsafe.com/zinsco_damage.aspx

Back to FPE:


http://inspectapedia.com/fpe/FPE_Fires_Waiting_to_Happen.php

http://www.ismypanelsafe.com/fpe.aspx


http://inspectapedia.com/fpe/FPE_History.php

FPE doesn't exist as the company it was, there still is a company with the name Federal Pacific, but not a direct tie in...confusing.
 
Yes it has been know for years about these two brands , plus push-a-matic is a three one. Now days, home inspector are telling home owners before a house is sold. These panels should be replaced. This is all good. :wave
 
Have seen many failed breakers thru the years. The brands mentioned have become notorious (and others). Many reasons i.e. moisture, particulate accumulation , environmental issues. These things don't last forever. Until recently, residential grade circuit breakers were not 'switch rated' that is, if you turned it on and off too many(nebulous) times, it is no longer effective! If you have a house with any of these discontinued brands, you might consider the older wiring to be problematical also. Hire a licensed electrician for advice. b
 
Have seen many failed breakers thru the years. The brands mentioned have become notorious (and others). Many reasons i.e. moisture, particulate accumulation , environmental issues. These things don't last forever. Until recently, residential grade circuit breakers were not 'switch rated' that is, if you turned it on and off too many(nebulous) times, it is no longer effective! If you have a house with any of these discontinued brands, you might consider the older wiring to be problematical also. Hire a licensed electrician for advice. b

Have seen people,do it them self, when they do not know what they are doing and make it a bigger mess. SAFETY FIRST AND FOLLOW THE RULES. Your last statement is VERY true.
 
OK, since we're talking electric panels, what about the compact single and 2-pole breakers? They're half the size of a traditional breaker.

While I'm using them, I'm a bit leery about the potential heat build-up. Are they a good idea, or bad?
 
They are call waffer breakers, if you use a name brand there are ok.. I never use less then 50% of the space for waffers.:wave Buss bars MUST BE clean and dry. No burnt marks.
 
They are call waffer breakers, if you use a name brand there are ok.. I never use less then 50% of the space for waffers.:wave Buss bars MUST BE clean and dry. No burnt marks.

Thanks.........I've always been a bit suspicious when things get smaller and lighter, but handle the same load.

However, I should be more concerned about how / why the electrician wired a 60A 2-pole breaker to the circuit that feeds my second floor receptacles and lights. Somewhere, I know, there's another panel/fuse box, but heck if I can find it.
 
Ignorance was bliss...

I have one of those FPE panels, which I assume accepts only FPE breakers? It's really the breakers that are the issue? Can another brand of breaker replace FPE breakers?

I rewired my whole house, which had a newly installed Federal Pacific Electric service panel. It looks like I'll be talking to an electrician soon.

Thanks for the tip.

Harry
 
Ignorance was bliss...

I have one of those FPE panels, which I assume accepts only FPE breakers? It's really the breakers that are the issue? Can another brand of breaker replace FPE breakers?

I rewired my whole house, which had a newly installed Federal Pacific Electric service panel. It looks like I'll be talking to an electrician soon.


Thanks for the tip.

Harry

The problem is there are no true new FPE's being produced, some brand may cross over, been awhile since I even thought of looking for one. Hear you can find them on EBAY but I wouldn't .
The buss bars the breakers stab into are also suspect .

Yeah, environmental conditions just make it worse...damp locations and salty fog along the coast was my headache:eek
 
Have seen many failed breakers thru the years. The brands mentioned have become notorious (and others). Many reasons i.e. moisture, particulate accumulation , environmental issues. These things don't last forever. Until recently, residential grade circuit breakers were not 'switch rated' that is, if you turned it on and off too many(nebulous) times, it is no longer effective! If you have a house with any of these discontinued brands, you might consider the older wiring to be problematical also. Hire a licensed electrician for advice. b

Welcome to the forum bp@sr9:wave

How many times have I seen small businesses using residential panels use breakers as on/off switches for lights, signage, kitchens and such.

There are several late 70's US Homes subdivisions built in the Houston/Pasadena area with Zinsco panels AND Alcoa Romex...and the original CVPC? plastic plumbing....RUN! My sister owns one as she bought before I was in the business to say don't and that stuff was new and cost effective.
She had it all reworked about five years ago as a retirement "gift" to herself.
 
All good info Steve. I'm not familiar with the FP panel trouble. Here, in the early 70's, there was aluminum wire (Romex) and back-stabed outlets (devices) that became the problem as things got older.
OM
 
And here I was planning on a good night's sleep......

It is kind of an OH GREAT moment for folks. I had not dealt with one in awhile.
Reading Harry's link from Angie's list comments has only a few saying Chicken Little. The guy who tried to test the breaker and burnt his screwdrivers tip smooth off had me :nod then :eek

The other guy who said just replace the breakers and be done as a panel is a panel is kinda in denial.

Yeah, the push- in easy back-stabbed outlets and switches were quick to install, but until the screw tightening versions came out, I still used the screw terminals on the older ones. Just didn't think those were a good solid connection. Especially with aluminum!
 
Aluminum

It is kind of an OH GREAT moment for folks. I had not dealt with one in awhile.
Reading Harry's link from Angie's list comments has only a few saying Chicken Little. The guy who tried to test the breaker and burnt his screwdrivers tip smooth off had me :nod then :eek

The other guy who said just replace the breakers and be done as a panel is a panel is kinda in denial.

Yeah, the push- in easy back-stabbed outlets and switches were quick to install, but until the screw tightening versions came out, I still used the screw terminals on the older ones. Just didn't think those were a good solid connection. Especially with aluminum!

Bolt on breakers are for commercial use and more expensive. Aluminum wires MUST be terminated correctly.
 
Bolt on breakers are for commercial use and more expensive. Aluminum wires MUST be terminated correctly.

OK, since you're spreading topics of interest......the 2 copper and single aluminum ground wire of the late 50's early 60's? Since we're only talking the ground wire in this case, is it much of a safety concern? My house is a post WW-II construction, so the early wiring is 2-strand copper, but later some of this 2-strand copper with Al ground was added and usually grounded to the receptacle box.
 
OK, since you're spreading topics of interest......the 2 copper and single aluminum ground wire of the late 50's early 60's? Since we're only talking the ground wire in this case, is it much of a safety concern? My house is a post WW-II construction, so the early wiring is 2-strand copper, but later some of this 2-strand copper with Al ground was added and usually grounded to the receptacle box.

I left my NEC code book behind, however, I believe the current code required a copper pigtail at the device which then can be wire nutted to the aluminum conductor. Is it aluminum or plated cu.?
I would imagine the set up you have may just have the al. under the brass ground screw. Some ground screws are cadmium plated which helps prevent galvanic corrosion from joining dissimilar metals...even though it still happens at cu.-al. pigtail. Copper salts will devour bare aluminum (unless treated properly with an inhibitor and weatherproofed) resulting in a failed connection.

A current knowledge response may be clarified by Eugene
 
I left my NEC code book behind, however, I believe the current code required a copper pigtail at the device which then can be wire nutted to the aluminum conductor. Is it aluminum or plated cu.?
I would imagine the set up you have may just have the al. under the brass ground screw. Some ground screws are cadmium plated which helps prevent galvanic corrosion from joining dissimilar metals...even though it still happens at cu.-al. pigtail. Copper salts will devour bare aluminum (unless treated properly with an inhibitor and weatherproofed) resulting in a failed connection.

A current knowledge response may be clarified by Eugene

The ground wire is aluminum and usually trapped under the pinch bolt on the wire clamp of the receptacle box (Raco brand style).
 
The ground wire is aluminum and usually trapped under the pinch bolt on the wire clamp of the receptacle box (Raco brand style).

Only needs to be grounded to the box if the box is metal, should also connect to the outlet. RACO make metal and non metal boxes. DO not connected Aluminum and copper wires together unless you know what you are doing!
 
Only needs to be grounded to the box if the box is metal, should also connect to the outlet. RACO make metal and non metal boxes. DO not connected Aluminum and copper wires together unless you know what you are doing!

Luckily............I haven't found any of that, so far.
 